Checked against its sources: Updated

Viessmann fault codes are mostly not explained to users: the Vitodens manuals read show a fault number but tell you to note it for the contractor, and define only a few displays such as CL and E3.12 The user manuals read don't list other numbers.

Covers
Viessmann Vitodens 050-W and 100-W/111-W, GB issues of 2026
You
Note the code, reset a burner lockout once, bleed radiators, and top up or call if pressure is below 1.0 bar.
A professional
Everything else. The manual says "Do not open the appliance." and "Do not remove casings."

1 Displays the manuals explain

Viessmann displays and what the user manuals say
Code or displayWhat the Viessmann manual saysWhich manual, pageWhat the Viessmann manual lets you do
CL with flashing warning triangleBurner locked out; burner doesn't start050-W (05/2026) pp25, 28-291Reset; notify the contractor if it recurs
Burner symbol with flashing fault numberBurner fault100-W (03/2026) pp29-30, 332Note the number, reset; notify the contractor if it recurs
Fault menu (Er)Lists fault messages; no numbers are defined050-W pp24, 28-291; 100-W p292Tell the contractor the code. OK only closes the message
E3 (shown "E 3" on 100-W)Holiday program or holiday at home on, via the app050-W p281; 100-W p332Check in the app, change or switch off
E10Connection to the home network can't be established050-W p201Check the router connection and network password
E12Connection to the server can't be established050-W p201Try the connection again later
"- - -" flashing three timesEmissions test mode not possible, low flow or low heat draw; not a fault you need to act on050-W p261; 100-W p312Nothing needed

The 050-W note says these codes appear in parts, first "E1" and then "0", so read the whole sequence before writing it down.1

2 How the reset works

Note the fault number first. Then press the up and down keys for about 4 seconds; a rotating bar shows the reset has started.1 Closing the fault display for now, or pressing OK on a message, is not a repair.1 Viessmann's warning is strong: "Do not reset the burner several times in quick succession", because faults left unrectified can have life-threatening consequences.1 Try once and then call the contractor.

3 Other checks in the manual

Below 1.0 bar the manuals say "Please top up with water or notify your heating contractor", but give no fill method or upper figure, so ask the contractor; see boiler pressure.12 For air, the same tables say to bleed radiators.12

4 Where these manuals don't fit UK advice

The GB-issue 050-W manual cites German rules and maintenance "at least every 2 years".1 That shouldn't be used as UK servicing guidance; see boiler service. The gas section gives no UK emergency number, so use the gas entry instead. The word condensate doesn't appear in the text of either manual, so there is no maker's method for a frozen pipe.

5 What wasn't covered

Only these two user documents, from Viessmann's UK library, were read, the 100-W in fewer places than the 050-W.3 Other Vitodens models weren't read and may differ.

Sources

  1. Operating instructions for the system user, Vitodens 050-W, 6173895 GB 05/2026, Viessmann read 3 November 2026.
  2. Operating instructions for the system user, Vitodens 100-W/111-W, 6167584 GB 03/2026, Viessmann read 3 November 2026.
  3. Viessmann UK technical documents library, ViBooks read 3 November 2026.