Skip to the entry
Boiler Look-Up
Subjects

Look-up › Fault codes by maker

Ideal boiler codes

Checked against its sources: Updated

Ideal boiler fault codes here come from two older user guides: letter codes on the Logic Combi and plain-English messages on the Logic+.12 Neither is the current issue and neither is hosted by Ideal, so check against your own guide.

Covers
Ideal Logic Combi and Logic+ Combi 24, 30, 35; Logic Max on web-page evidence only
You
Reset by the knob where the guide says, check the gauge and refill by the guide's loop method, check other gas appliances and prepayment credit.
A professional
Anything that fails after those steps. Ideal if under warranty, or a Gas Safe registered engineer outside it.

1 Fault displays

The table pairs each Logic code with the Logic+ message that has the same description; that pairing is by description only. "Contact" means Ideal if under warranty, otherwise a Gas Safe registered engineer.

Ideal fault displays, read from the two guides
Code or displayWhat the Ideal guide saysWhich manual, pageWhat the Ideal guide lets you do
F6 / Outside Sensor FaultOutside sensor failureLogic p71; Logic+ p172Reset, then contact
F7 / Low Mains VoltageLow mains voltageLogic p7; Logic+ p17Contact an electrician or electricity provider
F9 / PCB FaultUnconfigured PCBLogic p7; Logic+ p17Contact; no reset offered
L5 / Too Many Resets5 boiler resets in 15 minutesLogic p7; Logic+ p17Turn power off and on at the fused spur, then contact
L6 / Lockout 6False flame lockoutLogic p7; Logic+ p17Reset, then contact
C0 / Boiler Type Card FaultBCC activation faultLogic p7; Logic+ p18Reset, then contact
C2 / PCB ReplacementBCC faultLogic p7; Logic+ p18Reset, then contact
F1 / Low Water PressureLow water pressure; boiler won't run below 0.3 bar (Logic p4, Logic+ p11)Logic p7; Logic+ p18Check the gauge shows 1 to 1.5 bar; refill by the guide's loop method
L1 / Overheat LockoutFlow temperature overheat or no water flowLogic p7; Logic+ p18Check 1 to 1.5 bar; Logic+ adds bleed radiators, check radiator valves are open, reset
F2 / Flame LossFlame lossLogic p7; Logic+ p19Check other gas appliances work; check prepayment credit. Look at the meter valve only: if it is off, don't turn it on or reset, ring your gas supplier or an engineer; otherwise contact
L2 / Ignition LockoutListed with Flame Loss; failed ignition, which a blocked condensate pipe can cause, with gurgling firstLogic pp4, 7; Logic+ pp7, 12, 19As Flame Loss, and reset; thaw only as below
F3 / Fan FaultFan faultLogic p7; Logic+ p19Reset, then contact
F4 / Flow Thermistor FaultFlow thermistorLogic p7; Logic+ p19Reset, then contact
F5 / Return Thermistor FaultReturn thermistorLogic p7; Logic+ p19Reset, then contact
F4 / L4 (Logic)Flow thermistorListed on Ideal's website, not in the user manual read; L4 isn't in the 2013 table3The page suggests restarting, then contacting Ideal
Too Many Restarts (Logic Max)Too many restart attempts in a set periodListed on Ideal's website; no Logic Max manual read. Logic+ prints "Too Many Resets"4The page says power off and on at the fused spur, then contact
Outside Sensor Fault, Fan Fault, PCB Fault (Logic Max)Sensor; fan; PCB not configuredListed on Ideal's website; no Logic Max manual read4The page suggests restarting for the first two, then contact

2 Normal-running displays on the Logic Combi

Logic Combi status display, guide p61
DisplayMeaning
0Standby, no demand
C, burner light offHeating call, boiler already at set temperature
d, burner light offHot water call, boiler already at set temperature
C, burner light onHeating
d, burner light onHot water
P, burner light onPre-heat
F, burner light onFrost mode

3 How the reset works

Turn the mode knob to the reset position and immediately turn it back; there is no hold.12 The one exception is clearing a service reminder on the Logic+: hold at reset for 3 seconds.2 Try once, because five resets in 15 minutes becomes a fault of its own. Both guides also say a boiler with a known or suspected fault must not be used until an engineer has corrected it.12

4 Pressure and frozen pipes

Both guides give a filling-loop method and a 1 to 1.5 bar target; see repressurising. Both allow thawing a condensate pipe only if you feel competent, and never above ground level; see frozen condensate pipe.12 For a suspected gas leak, go to the gas entry.

5 What wasn't covered

Ideal's current Logic+ guide (215419-7) and Logic Max guide (219008-2) couldn't be retrieved, so newer boilers may show different wording. The user manuals read don't list other codes, and your own guide takes priority over this entry.

Sources

  1. Ideal Logic Combi 24, 30, 35 User's Guide, no document number in the copy read, file dated 17 July 2013, hosted by InspectApedia, not by Ideal read 3 November 2026.
  2. Ideal Logic+ Combi 24, 30, 35 User Guide, UIN 204979 A07, May 2014, hosted by Selco, a builders' merchant, not by Ideal read 3 November 2026.
  3. Logic Combi troubleshooting guide, Ideal web page, not a manual read 3 November 2026.
  4. Logic Max Combi troubleshooting manual, Ideal web page read 3 November 2026.