Look-up › Pressure and water

Pressure too high

Checked against its sources: Updated

Boiler pressure too high usually follows over-filling, a filling device letting water through, or a fault, and the safe response depends on the reading and your manual.1 Let the system cool and recheck before deciding.1

Covers
Sealed systems, UK. Figures are per named manual.
You
Let it cool, reread the gauge, close the filling device, bleed a radiator only if your own manual allows it.
A professional
Repeated rises, water from the relief pipe, a faulty vessel or filling device, anything inside the casing.

1 Read it cold first

Water expands when heated, so a higher reading with the heating on is normal, and Vaillant's website gives 3 bar as an upper limit while running1. Before doing anything, let the system cool, and compare with boiler pressure.

2 Three likely reasons

Vaillant's website gives three: too much water added during a recent top-up, an external filling device left not fully closed or passing water, or a fault in the boiler1. The first is easy to spot if you have just filled it. The second shows as a steady climb, covered under filling loop.

3 What the manuals say to do

The advice is not the same across makers, and Vaillant's own documents differ with age.

High pressure advice, by named document
DocumentReading it namesWhat it says
Worcester 4000, 2020/093Over 1.7 bar after over-fillingBleed one radiator back to 1-1.7 bar
Worcester i ErP, 2015/034Over 1.5 bar after over-fillingBleed one radiator back to 1-1.5 bar
Glow-worm Ultimate 3, 20195Too high, no figurePurge a radiator, or contact your competent person
Glow-worm Ultracom 2 cxi, 03/106High reading shownHeating off, open a radiator vent, or call
Vaillant ecoTEC pro, 20177No user figure for thisPurging is for the competent person
Baxi Platinum, 1/182Above 2.5 running; 3 or more is a faultContact installer or engineer as soon as possible
Main Eco Compact Combi8Above 3 barValve operates; disconnect a temporary loop; contact installer
Worcester Heatslave oil, 20109Above 2.5 barCause must be investigated; contact installer

Vaillant's website is broader than most: under 2.5 bar at room temperature needs no action, though bleeding will lower it, and over 2.5 bar it advises reducing the pressure before running the boiler, by bleeding or with help1. That differs from Worcester's stricter 1.7 bar on the 4000, which is why the manual for your own boiler comes first.

4 If your manual allows bleeding

Turn the boiler off first and let the radiators cool. Worcester's 4000 says not to vent with the heating on, and not to let pressure fall below its normal setting3. Watch the gauge while it comes down, and top up if you overshoot. The how-to is under bleeding a radiator.

5 When to call someone

Worcester's 4000 manual says pressure that keeps rising, especially if radiators keep needing to be vented, needs urgent action from a heating engineer, as it can mean corrosion in the system3. Do not cap or block the relief pipe to stop water coming out; it is a safety device.

Call as well if the reading climbs again after bleeding, or if water runs from the pressure relief valve pipe outside. Vaillant's leak page says to turn off the heating and water supply in that case and call an engineer, naming a faulty vessel or a passing filling loop as possible sources10. The expansion vessel entry covers that part.

Sources

  1. Vaillant, what pressure should a boiler be read 3 November 2026. Web page.
  2. Baxi Platinum 7697821-01, p6, section 3.1, 1/18, read 3 November 2026.
  3. Worcester 4000 manual 6720891170, pp9, 17, 2020/09, read 3 November 2026.
  4. Worcester i ErP manual 6720806946, p20, 2015/03, read 3 November 2026.
  5. Glow-worm Ultimate 3 instructions 0020239565_01, p15, read 3 November 2026.
  6. Ultracom 2 cxi user manual, Glow-worm, PDF p15, read 3 November 2026.
  7. Vaillant ecoTEC pro 0020244996_01, p12, 03.08.2017, read 3 November 2026.
  8. Main Eco Compact Combi 7716571-04, p17, read 3 November 2026.
  9. Heatslave oil manual from Worcester, p8, 03.2010, read 3 November 2026.
  10. Why a boiler leaks water, Vaillant read 3 November 2026. Web page.